I'm not sure how the entire setup of the model is done, but if, for example, you want your control variable for a temparture controller to be a heating device with an SI unit of W (watt) (it could be  or something similar depending on the model setup but let's assume W here). Then
 or something similar depending on the model setup but let's assume W here). Then K_P should have a unit of W/K, K_I should have a unit of W/(K*s), and K_D should have a unit of W*s/K. When you have set up the PID Controller with consistent settings, the deduced unit for the controller appears in the Information section at the bottom of the Settings window.
Best regards,
Magnus
                                                 
                                                
                            Hi,
I'm not sure how the entire setup of the model is done, but if, for example, you want your control variable for a temparture controller to be a heating device with an SI unit of W (watt) (it could be W/m^3 or something similar depending on the model setup but let's assume W here). Then `K_P` should have a unit of `W/K`, `K_I` should have a unit of `W/(K*s)`, and `K_D` should have a unit of `W*s/K`. When you have set up the PID Controller with consistent settings, the deduced unit for the controller appears in the **Information** section at the bottom of the **Settings** window.
Best regards,
Magnus                        
                                                
                                                                                                            
                                             
                        
                        
                                                
    
        Please login with a confirmed email address before reporting spam
     
    
 
                                                Posted:
                            
                                2 years ago                            
                            
                                22.11.2023, 13:10 GMT-5                            
                        
                        
                                                    Thank you very much Magnus for your replay and help.
It wokred.
                                                 
                                                
                            Thank you very much Magnus for your replay and help.
It wokred.